What is the title of Section 3 Part A in the Domestic Electrical Installer guidelines?
Electrical Testing
View source
What is the purpose of the tests mentioned in the Electrical Testing section?
To ensure
compliance
with BS
7671
View source
What is the prescribed sequence of electrical tests?
'Dead' Tests (supply de-energised):
Continuity of circuit protective conductors
Continuity of ring final circuit conductors
Insulation resistance
Polarity
'Live' Tests (supply energised):
External earth fault loop impedance (Ze)
Circuit earth fault loop impedance (Zs)
PFC & PSC
Testing of RCDs
View source
Why must the prescribed test sequence be followed?
Because each test's
satisfactory
outcome is necessary for the
subsequent
test
View source
What happens if there is a deviation from the prescribed test sequence?
It
negates
the testing
View source
What condition must all test equipment meet before use?
All test equipment must be
undamaged
and within
calibration
View source
What
precaution
should be taken during electrical testing?
Exercise extreme caution to avoid electric
shock
View source
What should be done once the testing has been completed?
Record
the results on a generic
schedule
of test results
View source
What is the purpose of 'dead' tests in
electrical
installations?
To ensure
continuity
of
circuit protective conductors
View source
What does the
continuity test
ensure between the
Consumer's Main Earthing Terminal
and the
Supply Earthing Arrangements
?
It ensures the consumer's main earthing terminal is at
earth potential
of
zero volts
View source
What facilitates the connection between the Consumer's
Main Earthing Terminal
and the earth potential?
The
Main Earthing Conductor
View source
What is the role of
Main Protective Bonding Conductors
?
To prevent extraneous conductive parts from rising above
earth potential
View source
What types of
extraneous conductive parts
are connected to the Consumer's
Main Earthing Terminal
?
Gas
,
water
,
oil service pipelines
,
structural steelwork
,
air-conditioning ductwork
, and
lighting conductors
View source
Why is
supplementary bonding
necessary in special locations like kitchens and bathrooms?
To prevent dangerous potentials existing between
extraneous conductive parts
View source
What do
Circuit Protective Conductors
&
RCDs
provide in an electrical installation?
A path for
Fault Current
to be safely carried away to earth
View source
What must be ensured about the
cables
during testing?
They must be
electrically continuous
throughout their length with no
breaks
View source
What can cause high
resistances
in
circuit protective conductors
?
A loose or corroded
connection
View source
What is the consequence of excessive
voltage drop
in cables?
It can lead to the
cable length
being too long
View source
What does the
instrument
used for testing provide?
A
resistance
reading in
ohms
(Ω)
View source
What does the
R1
+
R2
method involve?
Using the
line conductor
as a return path and involves two measurements
View source
What is the first step in the
R1 + R2 test method
?
Link L - E at the
consumer unit
and measure the
resistance
of the L-E loop
View source
What should be done with the
R1
+
R2
readings?
They should be recorded on the
Generic Schedule of Test Results
View source
What is confirmed while taking the measurement in the
R1 + R2 test
?
The
polarity
of the circuit
View source
What is the purpose of dividing the
L-N reading
by 2 in the
R1 + R2 method
?
To subtract the result from the
L-E loop reading
View source
What does
R1
represent in the context of the R1 + R2 test?
The resistance of the
Circuit Protective Conductor
(CPC) for that circuit
View source
What is the primary purpose of testing
protective conductors
?
To ensure that
continuity
exists
View source
What can the result of an
R1
+
R2
calculation also be used to determine?
The
earth fault loop impedance
at the accessory
View source
What are the key components involved in the
continuity
of circuit protective conductors?
Consumer's
Main Earthing Terminal
Supply Earthing Arrangements
Main Earthing Conductor
Main Protective Bonding Conductors
Supplementary Bonding Conductors
Circuit Protective Conductors
&
RCDs
View source
What are the steps involved in the
R1 + R2
test method
?
Link L - E at
consumer unit
and measure L-E
loop resistance
.
Record R1 + R2 readings.
Link L - N at consumer unit and measure L-N loop resistance.
Divide L-N reading by 2 and subtract from L-E loop reading.
Repeat for
remaining circuits
.
View source
What are the consequences of not ensuring
continuity
in circuit
protective conductors
?
Risk of
dangerous potentials
Potential for
electric shock
Failure of protective devices