  • A variety of demand factors reduce the connected load to the computed load.
  • Receptacles are typically installed with the grounding slot oriented downward.
  • For power systems of 600 V or less, fuses of a higher voltage rating can be applied on circuits of a lower system voltage.
  • Conductors must be protected in accordance with their ampacity.
  • The loads should be balanced on phase bus, as discussed earlier.
  • The amperes interruption current (AIC) rating for circuit breakers should be at least 5000 A and 10 000 A for fuses.
  • The current carried (amperage) by the electrical circuit or system protected by an OCP device must not exceed the maximum current rating of the circuit breaker.
  • In most commercial and industrial installations, several disconnects may be used.
  • In a single panelboard, not more than 42 overcurrent protection devices may be used for protecting lighting and appliance branch circuits.
  • The neutral (grounded) and grounding conductors are not protected by overcurrent protection.