Cards (19)

  • At what temperature should thermoplastic not exceed
    70°C at the conductor
  • At what temperature should thermosetting (XPLE) not exceed
    90°C at the conductor
  • The instillation methods & related reference methods
    • Method A: Cables in multi-core cables in a thermally insulated wall
    • Method B: Cables enclosed in trunking or conduit
    • Method C: Clipped direct
    • Method D: Cable laid direct in the ground
    • Method E/F: On a perforated tray
  • What are the Rating Factors
    • Ca
    • Cg
    • Ci
    • Cf
    • Ib
    • In
    • It
  • What is Ca
    Ambient temperature
  • What is Cg
    Grouping
  • What is Ci
    Thermal instillation
  • What is Cf
    For BS3036
  • What is ambient temperature
    Air temperature other than 30°C to be applied to the current capacities for cables in free air, given in Appendix F Table F1 rating factors
  • what are the types of grouping
    • Touching on a perforated tray system
    • Bunched
    • Enclosed
    • On a surface
  • What is thermal instillation

    • Cables in contact with a thermally conductive surface on one side
    • Material reduces the current-carrying capacity of any cable it may cover
  • What is rating factors used for 

    Its used to calculate a cable-size that must be applied where a BS3036 (rewireable) fuse is used
  • Voltage drop in consumer's instillations
  • Units
  • Current-carrying capacity formula
    1. Calculate the design current of the circuit to find(It≥In≥Ib)
    Ib = P/V = 6500/230 = 28.26 Amps = (round up) 30 Amps = In=30 Amps
    2. Find which rate factor we need to use
    3. 30/0.94 x 0.725 = 44.02A = It=44.02A
  • What is Ib

    Its the design current of the circuit (the current intended to be carried
  • What is In

    Its the rated current or current setting of protective device (CLOSES SIZE MCB
  • What is It

    Its the tabulated current-carrying capacity of a cable (Current that flow circuit)