0.392 - multiply the diameter of to get depth of equivalent area of rectangular gutter
0.8862 - multiply the diameter to get width of equivalent area of rectangular gutter
102mm/hr - rainfall intensity used around Manila and Environs
1.5x - minimum area of dome type strainers times the area of the outlet pipe
2x - minimum area of flat-surface type roof deck strainers for use on sun decks, parking decks times the area of the outlet pipe
Outlet connections are inside-caulked or female screwed
Cast-iron drain with integrally-cast water-stop ring around the outside of body - material for roof drains passing through the roof into the interior of a building
0.6m - Rainwater piping commencing 0.6 meter from the exterior of a building may be of suitable approved materials
Steel pipe or cast-iron - material at the bottom of the conductor draining over the catch basin as protection from damage
Gauge 26 Galvanized metal sheet - Rainwater downspout or conductor on the exterior side
150% - pressure test percentage used for the water pressure test
344.5 kpa - air pressure that may be substituted for the water test
15 minutes - duration that the test must withstand without leaking
Air Test - shall be used when there is a reason to believe that a drainage or plumbing system has become defective
15 minutes - duration that pressure must be held without introduction of additional air
3 days - notification to administrative authority that the work is ready for inspection
Pressure Test - shall ensure gastight and watertight connections
Drainage and Venting System shall be tested with water or air
At least the upper 3 meters height of the preceding section previously tested shall be tested again
15 minutes - duration that water is kept until inspection starts
Every 5th floor levels must have yoke vent
Size of yoke vent must be at least equal to soil stack or vent stack whichever is smaller
1m - yoke vent connection with the vent stack above the floor level
Must connect with the drainage stack via wye branch
10 or more stories above the building drain shall be served by a parallel vent stack
0.15m - extension of vent pipe above the roof
0.30m - clearance of a vent pipe through roof away from any vertical surface nearby
3m - horizontal distance of vent opening from any openable window, door opening, air intake or vent shaft
0.9m - vertical distance above vent opening from any openable window, door opening, air intake or vent shaft
0.9m - horizontal distance of vent opening away from lot line, alley, and street boundary lines
0.15m - height extension of vent pipe above roof or fire wall
3m - horizontal distance of vertical vent pipes for outdoor installations to any part of roof that is used for other purposes
2.1m - vertical distance of vertical vent pipes for outdoor installations to any part of roof that is used for other purposes