x diameter Minimum airgap for fixtures not affected by side walls in reference to effective opening
3
x diameter Minimum airgap for fixtures affected by side walls in reference to effective opening
150 mm
Minimum distance of Atmospheric Vacuum Breaker (AVB) above all downstream piping and floor level rim of receptor.
30.5 cm
Minimum space clearance between the lowest portion of the assembly and the grade, floor or platform for access and clearance.
30.5 cm
Minimum distance of Double Check Valve assembly above all downstream piping and floor level rim of receptor.
152 mm
Minimum distance of Spill-Proof Pressure-Type vacuum breaker above all downstream piping and floor level rim of receptor.
1.52 m
Elevation of installations above the floor or grade to be provided with a permanent platform.
25 mm
Minimum air gap for water distribution, or a minimum of 2 pipe diameters.
152mm
Installation of atmospheric vacuum breaker above the flood level rim.
43.3° C
Minimum temperature for backflow prevention device to operate without rendering any portion inoperative.
152 mm
Minimum height of the AVB critical level above the overflow rim of a water closet bowl or the highest part of a urinal.
25 mm
Minimum height of ballcock's critical level above the full opening of the
overflow pipe.
152 mm
Minimum installation height of listed non-removable hosebibb-type backflow preventer above the highest point of usage.
51 mm
or smaller Size of cast iron fittings to be galvanized when used in water piping.
8%
Maximum lead content for water pipes and fittings
14 to 18
Number of mesh per 25 mm for gravity tanks vent screen.
less than 103 kPa
Inadequate water pressure
more than 551 kPa
Excessive water pressure
80%
Percentage of the reduced pressure used for all pipe size determination.
1033 Ра
Maximum pressure setting of pressure relief valve.
152 mm to 600 mm
Height of the drain pipe of pressure relief valve above the ground and pointing downward.
0.30 m
Distance between bottom of water pipe and top of the sewer or drain line.
0.30 m
Horizontal distance between the water line and the sewer or drain line.
0.30
m Distance between
sewer
or drainage piping and water pipes crossing above such drainage pipes.
0.30 m Maximum distance of
unions
away from regulating equipment,
water heater
, conditioning tank or similar.
19
mm dia Minimum size of
water service pipe.
4 feet
Maximum intervals of piping supports, based on Chapter 6.
3 feet
Support trap arms in excess of in length shall be as close as possible
1/4 inch
Closet rings shall be tightly fastened up to the floor with top surface above finish floor.