Cards (15)
15 cm
Minimum height of galvanized iron or galvanized steel pipe above the ground
152 mm
Minimum rise of each vent above the highest flood level rim before offsetting horizontally to join the vent stack or stack vent.
1 pipe size increase
Increase in size of vent stack above the reconnection point of stack and horizontal vent.
15 cm
Minimum extension of a vent pipe above the roof or fire wall
0.30 m
Minimum clearance of a vent through roof from any vertical surface nearby.
3 m
Horizontal distance of a vent opening away from any openable window, door opening, air intake or vent shaft.
0.90 m
Vertical distance of a vent opening above any openable window, door opening, air intake or vent shaft.
0.90 m
Horizontal distance of a vent opening away from any lot line, alley and street boundary lines.
3 m
Horizontal distance of vertical vent away from any part of the roof that is used for other purposes.
2.1 m
Vertical extension of a vent above any roof that is used for other purposes.
10
Each soil or waste stack which extends or more stories above the building drain shall be served by a parallel vent stack.
every 5 floors
Intervals of yoke vent.
not less than 1 m
Yoke vent connection with the vent stack above the floor level.
32 mm
Minimum size of an individual vent, or not less than 1/2 the diameter of the drain to which it is connected.
1/3 Fraction
of the total permitted length of any vent allowed to be installed in a horizontal position.