Chapter 9

Cards (15)

  • 15 cm Minimum height of galvanized iron or galvanized steel pipe above the ground
  • 152 mm Minimum rise of each vent above the highest flood level rim before offsetting horizontally to join the vent stack or stack vent.
  • 1 pipe size increase Increase in size of vent stack above the reconnection point of stack and horizontal vent.
  • 15 cm Minimum extension of a vent pipe above the roof or fire wall
  • 0.30 m Minimum clearance of a vent through roof from any vertical surface nearby.
  • 3 m Horizontal distance of a vent opening away from any openable window, door opening, air intake or vent shaft.
  • 0.90 m Vertical distance of a vent opening above any openable window, door opening, air intake or vent shaft.
  • 0.90 m Horizontal distance of a vent opening away from any lot line, alley and street boundary lines.
  • 3 m Horizontal distance of vertical vent away from any part of the roof that is used for other purposes.
  • 2.1 m Vertical extension of a vent above any roof that is used for other purposes.
  • 10 Each soil or waste stack which extends or more stories above the building drain shall be served by a parallel vent stack.
  • every 5 floors Intervals of yoke vent.
  • not less than 1 m Yoke vent connection with the vent stack above the floor level.
  • 32 mm Minimum size of an individual vent, or not less than 1/2 the diameter of the drain to which it is connected.
  • 1/3 Fraction of the total permitted length of any vent allowed to be installed in a horizontal position.