The occupant load for any building or part of a building is calculated by dividing the floor area designated for a specific use by a unit area allowed per occupant
The exit requirements for a building or its portions are determined by the occupant load that results in the largest number of people
Rooms with an occupant load of more than 50 people (where fixed seats are not installed) and are used for purposes like classrooms or assemblies should have the room's capacity (the maximum number of people it can safely hold) posted in a conspicuous location near the primary exit
Changes in floor elevations of less than 300 millimeters along any exit serving a tributary occupant load of 10 or more should be accomplished using ramps
Every building or usable portion must have at least one exit
Floors above the first storey with an occupant load of more than 10 must have at least two exits
Mezzanine floors used for purposes other than storage, if exceeding certain size criteria, must have at least two stairways to an adjacent floor
The total width of exits, measured in meters, must not be less than the total occupant load served divided by 165
If only two exits are required, they should be a distance apart equal to at least one-fifth of the perimeter of the area served, measured in a straight line between exits
Without a sprinkler system, no point in a building should be more than 45.00 meters from an exterior exit door, a horizontal exit, exit passageway, or an enclosed stairway, measured along the line of travel
Exit doors must swing in the direction of exit travel when serving hazardous areas or when serving an occupant load of 50 or more
Exit doors should be open-able from the inside without the use of a key or special knowledge or effort
Required exit doorways should be of a size allowing the installation of a door that is at least 900 millimetres wide and at least 2.00 metres in height
No leaf of an exit door should exceed 1.20 metres in width
Revolving, sliding, and overhead doors should not be used as required exits
There should be a floor or landing on each side of an exit door, leveled with or not more than 50 millimetres lower than the threshold of the doorway