Its the name give to the wide range of electrical components, from the common fuse to more complex devices as circuit breakers and residualcurrentdevices
Protective devices are installed to protecttheinstillation from shortcircuiting or overloading, either by blowing or tripping
What is a short circuit
its an overcurrent resulting from a fault of negligible impedance between conductors having a difference in potential under normal operating conditions
What is overload
When an electrical circuit or device exceeds the current or power level of its intended designed capacity
What are the two ways a protective device works
Heat
The device gets hot and melts or it bends a bimetallic contact, opening a switch
Magnetic
With an increase in current there is an increase in the magnetic field. this increases due to a metal rod to move and thus operate the switch
What is Current rating
Its the maximum current that a protective device will carry indefinitely without the device operating or being damaged
What is Fusingcurrent
Its the minimum current that will cause a protective device to operate
What is Fusingfactor
Its the ratio of fusing a current to current rating
What is the formula for fusingfactor
Fusingfactor = fusing current / current rating
The purpose of overcurrent protection
The consumer's mains equipment must provide protection against overcurrent, that is, acurrent exceedingtherated value (IETRegulation430.3)
Protective devices provide overcurrent protection when situated in the line conductors; they must not be connected in the neutral conductor.
Circuit breakers may be used in place of fuses, in which case the circuit breaker may also provide the means of isolation, although a further means of isolation is usually provided so that maintenance can be carried out circuit equipment.
When selecting a protective device we must give consideration to to the following factors
The prospective fault current
The circuit load characterises
The current-carrying capacity of cable
The disconnection time requirement for the cable
The essential requirements for a device designed to protect against overcurrent are
It must operate automatically under fault condition (know as A.D.S)
It must have a current rating attached to the circuit design parameter (should be under 0.45 second)
It must have a disconnection time which is in the design parameters
It must have adequate faults breaking capacity
It must be suitably located and identified
What is the BS number for protective devices
BS3036
what are the disadvantages of renewable fuses
Incorrect element sizecanbeinstalled
element cannot be repaired quickly
Element deteriorates with age
Poor discrimination
can cause damage during very high fault current faults.Poor breaking capacity
Can be dangerous when inserted, a fault is still on an instillation
What is the advantage of cartridge fuses
No moving parts
Small physical size
Reasonably accurate current rating
Not liable to deterioration with age
What is the disadvantages of Cartridge fuses
Incorrect cartridge can be installed in plug tops
More expensive than renewable
Not suitable for very high fault current
Can be shorted out using silver foil
What is the BS number for cartridge fuses
1361/62 (now BS88-3)
What is the BS number for HRC cartridge fuses
BS88
The advantages of HRC cartridge fuses
Discrimination between short duration overloads and high fault current
Simple to observe when the fuse has blown
Accurate current rating
Consistent in operating - every fuse in the box is the same
not liable to deterioration
The disadvantages of HRC cartridge fuses
Expensive
Can be replaced with a larger fuse rating
What is the two meanings of circuit breaker
Magnetic
Thermal
What is the advantages of circuit breakers
Tamperproof
Simple to observe when the circuit breaker has tripped
Supply can be quickly restores
Pre-set tripping characteristics can't be altered
Can differentiate between short and prolonged overload
Single as well as multi-pole units
What is the disadvantages of circuit breakers
Expensive
Regular testing is necessary to guarantee safe operation
Having moving parts
Variants in temperature affects the operation
What are the other types of miniature circuit breakers
TypeB - circuit breakers are used in domestic settings and for purely resistive loads
Type C - circuit breakers are used for moderately inductive loads (loads with coils in like motors and discharged lights, like fluorescent luminaires)
Type D - circuit breakers are used in highly inductive circuits like welding transformers and x-ray machines
what is breaking capacity
To measure the total current that a protective device can handle during a fault without blowing apart
thecurrent rating of the device will tell how much current will indefinitely flow without causing the device to operate
Theenergyletthroughclass is a measure to how much energy will pass through the device before it operates
Thetype gives a choice depending on the nature of the connected load
The breaking capacity is a measure of the total current that a protective device can handle during a fault
MCB - The current rating - of the device will tell how much current will indefinitely flow without causing the device to operate at its maximum power
MCB - The energy let through class - is a measure to how much energy will pass through the device before it operates
MCB - Thetype - gives a choice depending on the nature of the connected load
MCB - Thebreakingcapacity - is a measure of the total current that a protective device can handle during a fault
What are the 4 types of protective devices
Renewable fuses (also called semi-enclosed fuses)
Cartridge fuses
HRC or HBC fuses
Circuit-Breakers
What is the purpose of a Renewable (semi-enclosed) fuse-BS3036
If the current is too great for the rating, the fuse will be unable to dissipate the heat, and fuse wire will melt
This type of fuse is only good for current up to 100A and voltage up to 250V
The advantages of a Renewable (semi-enclosed) fuse - Bs3036
No moving parts
Cheap
Melted element is easy to se
Low replacement cost
What is a Cartridge fuse
This is a very common fuse found in distribution boards, consumer units(ccu), plug tops and small control circuits
What is a HRC cartridge fuse - BS88
This type of fuse is quite expensive and is commonly used in industry
What is the purpose of a circuit breaker
It has 2 meanings: Thermal & Magnetic
The current flows and neither the bi-metallic trip nor the magnetic trips are affected
The latching mecanism is held in place and the pluger is low, not affecting the trip mechanism
What are the names given to maximum current that can flow under both Earth fault and Short circuit conductors
Prospective earth-fault current
Prospective short-circuit current
What happens when a Renewable fuse is installed
When a current flows in a circuit is given off
If the current is greater than the rating, the fuse will be unstable to dissipate the heat and the fuse will melt
The type of fuse is good for current up to 100A and voltage up to 230V