A.c. power is converted into d.c. power at the sub-station by using converting machinery e.g. mercury are rectifiers, rotary converters and motor-generator sets
The load voltage goes on decreasing as we move away from one feeding point, reaches minimum value and then again starts rising and reaches maximum value when we reach the other feeding point
The minimum voltage occurs at some load point and is never fixed
If a fault occurs on any feeding point of the distributor, the continuity of supply is maintained from the other feeding point
In case of fault on any section of the distributor, the continuity of supply is maintained from the other feeding point
The area of X-section required for a doubly fed distributor is much less than that of a singly fed distributor
Whenever possible, it is desirable that a long distributor should be fed at both ends instead of at one end only, since total voltage drop can be considerably reduced without increasing the cross-section of the conductor
Distributor A B fed at both ends with equal voltages V volts and having concentrated loads I1, I2, I3, I4 and I5 at points C, D, E, F and G respectively
As we move away from one of the feeding points, say A, p.d. goes on decreasing till it reaches the minimum value at some load point, say E, and then again starts rising and becomes V volts as we reach the other feeding point B
All the currents tapped off between points A and E (minimum p.d. point) will be supplied from the feeding point A while those tapped off between B and E will be supplied from the feeding point B