  • more than 1.5m, less than 4.6 m Length of indirect waste pipe to be directly trapped, but need not be vented.
  • Less than 4.6 m Length of indirect waste pipe need not to be larger in diameter than the drain outlet or tailpiece.
  • 13 mm dia Minimum diameter of indirect waste pipe.
  • 0.45m to 0.80m Extension of standpipe receptor for clotheswasher above its trap.
  • 15 cm to 45 cm Height of the trap for clotheswasher standpipe receptor above the floor.
  • 60 °C Maximum temperature allowed for water to be discharged under pressure directly into the drainage system.
  • 152 mm For condensers and sumps, the extension of the deep seal trap to within the bottom of the trap.
  • 19 mm dia For condensers and sumps, diameter of the opening serving as siphon breaker at the top of the deep seal trap.
  • 1/2 Outlets shall be taken off from the side in a manner to allow a water line to be maintained that permanently occupies not less than the capacity of the condenser or sump.
  • 102 mm Minimum thickness of walls and bottom of sumps, condensers or intercepting tanks constructed of concrete.
  • 13 mm Minimum thickness of plaster on the inside walls of sumps and condensers, etc.
  • GA 12 (2.77 mm) Minimum thickness of metal condensers.
  • 102 mm Sumps and condensers shall contain a volume of not less than twice the volume of water removed from the boiler connected thereto when the normal water level is reduced not less than
  • 3.2 mm Minimum thickness of chemical-resistant glass lined pipe, high silicon iron pipe or lead pipe receiving acid or corrosive chemicals.
  • 1 and 2 F.U. Fixture unit limit of wet venting.
  • 4 fixtures Maximum number of fixtures can be served by a vertical wet vent.
  • 1 pipe size larger; 51 mm dia Minimum size of wet vent.
  • 152 mm Connection of the returned vent for island fixtures to the horizontal drain above the flood level rim
  • more than 4.6 m In CW & VS, length of branch that must be separately vented.
  • 2 pipe sizes larger Minimum size of waste pipe and trap in any CW & VS, in reference to the sizes required and tailpiece size
  • 0.60 m Maximum length of tailpiece
  • 51 mm dia Cleanouts may not be required on any wet-vented branch serving a single trap when the fixture tailpiece or connection is larger than