150 mm
Minimum diameter of building sewer, but not less than the size of the building drain
2%
Recommended slope for building sewer.
1%
Allowable slope for drainage piping 102 mm or larger in diameter given the site constraints.
0.5%
Allowable slope for drainage piping 203 mm or larger in diameter.
0.60 m
Distance of the building sewer from the outer face of any building foundation or wall.
0.30
m Minimum depth of building sewer below the finish surface of the ground
exceeding 135°
Aggregate offset angle to be provided with an additional cleanout.
less than 3 m
Length of building sewer not requiring for a cleanout.
91 m
Maximum distance between manholes
0.30 m
Distance between bottom of water pipe and top of the sewer or drain line
0.30 m
Horizontal distance between the water line and the sewer or drain line
0.30 m
Distance between sewer or drainage piping and water pipes crossing above such drainage pipes.
3 m
Minimum distance of water pipe joints away from a sewer line.
1.5 m
Distance within the property line where every abandoned building sewer shall be plugged or capped.
30 days
Maximum number of days from the time of connection to the public sewer an abandoned disposal facility shall be filled.
0.60 m
Minimum horizontal distance of a building or structure from the building sewer.
15.2 m
Minimum horizontal distance of water supply wells from the building sewer.
7.6 m
Allowable reduction in distance between water supply wells and building sewer when constructed of approved materials for use within a building.
15.2 m
Minimum horizontal distance of streams from the building sewer.
0.30 m
Minimum horizontal distance of on-site domestic water service line from the building sewer.
0.30 m
Minimum horizontal distance of public water main from 3 m - Appendix B the building sewer.